Electrical questions come up constantly, and the answer is almost always on the outdoor unit's rating label. Here's how to read it.
MCA and max fuse- MCA (Minimum Circuit Ampacity) tells your electrician the minimum ampacity for the circuit wire.
- Max fuse / MOP (Maximum Overcurrent Protection) is the largest breaker or fuse allowed on that circuit.
For example, the 2026 catalog lists the 12K Hyper outdoor unit (CH-RHP12-230VO) at 15 A MCA and a 15 A max fuse. The 24K Hyper (CH-RHP24-230VO) is 24.9 A MCA with a 25 A max fuse. Always go by the label on your own unit, since models and revisions differ.
What the installation manual asks forThe installation manual (https://media.cooperandhunter.us/2809/Installation-Manual.pdf) for current wall-mounted models says:
- Use a dedicated branch circuit for the unit, with nothing else on it.
- Fixed wiring needs an all-pole disconnect switch or breaker with at least 1/8 in (3 mm) contact separation.
- Ground the unit properly.
- All wiring must meet local and national codes and be done by a licensed electrician.
Most local codes also want a service disconnect within sight of the outdoor unit.
Line setsLine size depends on capacity. On current single-zone units it's 1/4" x 3/8" for 6K to 12K, 1/4" x 1/2" for 15K and 18K, and 3/8" x 5/8" or larger above that. Check your model's table to be sure. Current single-zone units are precharged for 25 ft. Longer runs need extra refrigerant added by a tech, and every model has a maximum length and height difference. Keep the run to at least 10 ft, insulate both lines, and protect the insulation from UV.
What breaker, wire size and disconnect did your electrician use, and how long is your line set?